Basic rules of workplace lighting

Lighting design

Working at a screen places high demands on the eyes. A few rules can help in designing office workplaces well.

Horizontal illuminance 

An important parameter in lighting design is illuminance, measured in lux (lx). The rule is: the more demanding the visual task, the higher the illuminance required. At a minimum, the following reference values should be observed:

Illuminance: Recommended minimum values (Graphic: © IBA)
Illuminance: Recommended minimum values (Graphic: © IBA)

Area

Examples according to ASR A3.4

Lux

General room lighting 

Filing, copying

300

Workplace lighting

Writing, reading, data processing

500

Task lighting (localised)

Technical drawing (hand drawing)

750

Special areas

Archives

200

Infoblock Symbol

Measurements are taken at a height of 0.75 m above floor level. 

Infoblock Symbol

The illuminance values given above are minimum requirements. Higher levels may be advisable, particularly for older employees. At the very least, a desk lamp should be provided. A controllable overall lighting system is recommended.

Infoblock Symbol

It should also be considered that illuminance levels decrease over time due to ageing and soiling of lamps. Depending on the maintenance factor, installation with higher illuminance levels may therefore be necessary. Higher levels are also advisable when the visual task places particularly high demands on the eyes.

Illuminance

Illuminance alone is not sufficient to describe the effect of light. The actual perceived brightness depends largely on the reflection of light from surfaces at and around the workstation. At identical illuminance, the impression of brightness is significantly higher over a white surface than over a grey one. This effect is expressed in the measure of luminance (L), measured in candela per square metre (cd/m²).

Relationship between illuminance and luminance (Image: © IBA)
Relationship between illuminance and luminance (Image: © IBA)

Excessive luminance leads to glare. More on this can be found in the corresponding chapter.

Infoblock Symbol

Light-coloured surrounding surfaces make rooms appear brighter. However, surfaces at the workstation should not be too bright and, above all, not glossy – as both can cause reflected glare.

Luminance ratio

At the workplace and in its surroundings, a balanced luminance ratio between all surfaces is also important. Strain-free (stable) visual perception is ensured when the luminances of the visual task area (the task field, e.g. monitor or document) and of the surrounding surfaces (the background, e.g. walls, ceilings, windows, but also the room’s lighting systems) are within a ratio of 1:2 to 1:10 from task field luminance to background luminance.

Infoblock Symbol

DIN 5035–7 permits luminance ratios of more than 10:1 for the wider visual field. However, this leads to increased mental strain.

Colour rendering

In addition to sufficient brightness and glare-free conditions, an accurate impression of the illuminated objects is important. This is determined by the colour rendering index Ra. This dimensionless value classifies the colour rendering quality of lamps and can range from 0 to 100, with 100 representing absolutely faithful colour rendering. For office environments, ASR A3.4 requires a minimum value of 80 Ra.